The control valve receives signals from the DCS that allow it to be opened fully or closed fully only; it cannot be set at positions such as halfway or 75%

2021-06-11View Original

Thread Content

When tuning the pneumatic control valve, it can only be opened to 25%, 50%, and 75% – it won’t open at any other setting. I would appreciate it if experts could advise me on how to adjust it
Reply #22021-06-11
Could you be more specific with your question? Are you referring to the on-site locator? Send a manual signal at the locator site to see what happens
Reply #32021-06-11
Measure the input signal to the control valve; if the input signal is correct but the valve does not operate properly, then check the valve
Reply #42021-06-11
It is this type of control valve: at present, it can only be operated to the fully open or fully closed position; it cannot even be opened to half the signal level
Reply #52021-06-29
There must be something loose in that locator; there’s no negative feedback
Reply #62021-06-29
Re-calibrate the locator; with mechanical positioning, it’s necessary to adjust the zero and full positions repeatedly. If possible, switch to an intelligent locator or a semi-mechanical one, as this will significantly reduce the amount of maintenance required

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.