There is a PT100 thermal resistor connected to the Rosemount 3051 transmitter on site, but the transmitter has no temperature output display. Remove the thermal resistor wiring at the transmitter end, and there is no problem in measuring the resistance. Use a loop calibrator to connect it to the transmitter to simulate the PT100 resistance value. After the transmitter temperature shows normal, remove the PT100 resistor and connect it next to the transmitter. The transmitter temperature displays normal and the transmitter is inserted into the casing. There is still no display of the transmitter temperature.
Reply #22021-06-23
Thermometer Troubleshooting, Transmitter Troubleshooting, Line Troubleshooting Where is the problem?
Reply #32021-06-23
pt100 then 3051? Isn't 3051 a pressure transmitter?
Reply #42021-06-23
First of all, you have to determine whether your transmitter is pressure or temperature. In my impression, temperature transmitters are generally integrated. I have never seen separate ones, unless the PT100 is connected to a secondary meter for display.
Reply #52021-06-23
Let’s use the simplest and most effective method. Take the thermal resistor, transmitter, and bushing and replace these combinations to see where the fault is.
Reply #62021-06-23
Try changing the cable from the thermal resistor to the transmitter.
Reply #72021-06-23
Since there is no problem connecting the removed thermal resistor to the temperature changer, the only thing left to do is to check the line between the thermal resistor and the temperature changer.
Reply #82021-06-23
“Use a loop calibrator and connect it to the transmitter to simulate the PT100 resistance value. After the temperature of the transmitter is normal, remove the PT100 resistor and connect it next to the transmitter. The temperature of the transmitter is normal." Also, the line from PT100 to the transmitter has not been checked.
Reply #92021-06-23
You came out to cause trouble, Rosemount temperature change 644/248, you made 3051 pressure transmitter to fool everyone. . . If such a simple problem cannot be solved, there is not much room for technological development in this industry.
Reply #102021-06-23
This post was last edited by chensf123 on 2021-6-23 23:11. Are you sure you are using a 3051 pressure transmitter connected to a thermal resistor? If confirmed, it is indeed an epic problem.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.