For a level sensor, as long as it is connected to the card, the current will be abnormal; however, there is no problem with the current as long as it does not pass through the card. But using a different temperature transmitter works just fine. A better level transmitter will also work just fine. Is it the issue of cheap level gauges? Is the interference resistance weak?
Reply #22022-04-16
How can current be measured without a current clamp? Four-wire system? Was it measured at the instrument side or at the cabinet side? Have you tried switching channels?
Reply #32022-04-16
Power distribution for the two-wire system signal generator – I’ve checked both the field site and the cabinet; the wiring is fine. I even changed the channels, but the problem persists
Reply #42022-04-16
Changing the sensor will solve the problem; is there a solution?
Reply #52022-04-16
What are the specific specifications of the level sensor (number of wires, power consumption, etc.)?
Reply #62022-04-16
Two-wire, 4-20ma, output resolution of 1uA, power consumption
Reply #72022-04-16
Have you tried powering it separately, without using the card circuit for power supply (by connecting the card in a passive manner)?
Reply #82022-04-16
It’s possible that there is a problem with the internal circuit of the level gauge, and the current power supply isn’t sufficient to drive it.
Reply #92022-04-16
I’ve tried it; it works fine when powered separately, but I don’t understand why
Reply #102022-04-16
I haven’t tried it with a passive card connector; I’ll give it a try
Reply #112022-04-16
Actually, it’s not necessary; it’s fine to just use a different sensor

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.