「Discussion on the selection of measurement range for differential pressure level measurement.

2017-07-15View Original

Thread Content

As the title suggests, is it possible to select a height within the range of the upper and lower flanges as the measurement range as needed?
Reply #22017-07-15
Sure. If only half of the slot needs to be measured, set it from the top to half of the slot.
Reply #32017-07-15
Yes, you can choose a differential pressure transmitter with a range that is close to the differential pressure value calculated based on the upper and lower flanges. During debugging, set the range on-site to perform zero-point adjustment
Reply #42017-07-15
Yes, you can choose a differential pressure transmitter with a range that is close to the differential pressure value calculated based on the upper and lower flanges. During debugging, set the range on-site to perform zero-point adjustment

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.