2025-11-28View Original

Thread Content

In the SIS, there is interlocking for pump failure signals; considering fault safety, should a normally closed signal from the electrical system be used, so that the normal operating contact of the pump remains closed while its failure contact opens?
Reply #22025-12-02
The pump failure signal should be connected to normally closed contacts (NC) first, to ensure that the SIS automatically enters a safe state in the event of a wire break or equipment failure. If the device only supports normally open contacts (NO), logical inversion and redundant design are required, while HAZOP/LOPA analysis is used to verify whether the risks are acceptable
Reply #32025-12-02
The unit PLC signals have been sent over.
Reply #42025-12-07
There is no need for pump fault signals to be sent to the SIS. Pumps generally have backup units; if the pump is a critical piece of equipment, then the stop signal can be sent to the SIS 2oo2

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.