On the synthesis furnace, the hydrogen orifice plate flow meter gradually shows an increasing reading every other half day; the reading is about 200 units higher than the actual flow rate. When water is released from the three-valve assembly, the situation returns to normal, but the reading increases again after another half day. Even after replacing the flow meter’s gauge head, the same problem persists. There was no solution other than shutting down the furnace and examining the orifice plate, which showed no signs of deformation. The pressure pipes were also cleaned using air supply tubes, and there was no blockage. A new gauge head was installed, and after zeroing the meter with the three-valve assembly closed, and with no flow in the pipeline, the reading still increased to -126 after a day. I’m really puzzled – what could be causing this issue? With other furnaces that are shut down, the flow meter doesn’t show any change at all. I earnestly request help from experts; thank you very much
Reply #22025-12-11
In my opinion, this phenomenon is due to the fact that the positive pressure measurement isn’t flowing smoothly – there’s a blockage, but it’s not a complete blockage.
Reply #32025-12-11
The last edit to this post was made by ssln123 on 2025-12-12 at 10:08: 1 Try replacing the three-valve assembly. 2 If possible, try connecting a temporary cable. 3 Try using a different digital display unit for control to identify the issue step by step
Reply #42025-12-12
In your case, it’s most likely an issue with the three-valve assembly or the transmitter. Is it because of the hydrogen you measured? Diaphragms that are not gold-plated are prone to hydrogen embrittlement and need to be replaced regularly; the simplest solution is to replace them all.
Reply #52026-03-20
That’s right, I think the same way. A low-flow meter cut-off can be set in the table header.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.