Please tell me, the regulations require that a UPS room, engineer room, air conditioning room, etc. should be set up in the local cabinet room. In that small cabinet room, if there is no engineering station and the UPS capacity is less than 10kva, is it still necessary to set up these rooms?
Reply #22026-07-09
The word "appropriate" in the specification is indeed confusing. I understand that you are worried that it will waste space or cost if the small cabinets are installed according to the specification. In fact, in actual projects, small cabinet rooms like this (no engineering station, UPS capacity <10kVA) can usually be handled flexibly.: UPS room: As long as the UPS is not a lead-acid battery that requires separate ventilation and explosion protection, it can generally be placed in the same room as the cabinet, but attention should be paid to heat dissipation and spacing. It is recommended to leave space for maintenance. Engineer's room: If there are no permanent debugging personnel on site, or maintenance can be done remotely, it is completely unnecessary. The "appropriate" in the specification is not mandatory, but you need to evaluate whether remote diagnosis is feasible. Air conditioning room: It also depends on the amount of heat generated. For a small cabinet, an ordinary precision air conditioner or wall-mounted unit can be placed directly indoors without the need for a separate compartment, but don’t forget to check whether the cooling capacity is sufficient. It is recommended that you read GB 50174-2017 "Data Center Design Specifications" or the special provisions for "small computer rooms" in industry standards. Different industries (such as chemical industry, communications) will have supplementary regulations. If you are not sure, it is best to ask someone with an electrical or HVAC professional from the design institute to confirm. After all, safety comes first.
Reply #32026-07-15
It is recommended to set up at least one cabinet room and one engineer room in the on-site cabinet room. A UPS with a capacity of less than 10kva can be placed in the cabinet room. However, the instruments generally use lead-acid batteries. During the review and acceptance of many projects, experts have proposed to make anti-explosion design in accordance with the requirements of GB50172, so it is recommended to set up a separate UPS room if conditions permit. The engineer room is generally necessary to facilitate configuration, debugging and later maintenance during the construction phase. SH/T3092 also requires that the on-site cabinet room be equipped with at least one on-site engineer station. Other rooms, such as air-conditioned rooms, do not need to be installed and can use cabinet air conditioners.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.