We currently have a 7.5kw motor rated at 380V50HZ, but the voltage at the site is 440V50HZ. If I change the connection from delta to star, what will be the new rated power? What will the rated current be? Motor nameplate: 380/660, Delta/Y, 7.5kw, 15.7A
Reply #22018-03-11
Changing from corner connection to star connection – doesn’t that reduce the current at the cost of increased power consumption?
Reply #32018-04-04
Based on the conditions you provided of 7.5 KW and 380 V, the power factor is calculated to be 0.7. After changing it to star connection and applying a 440V voltage, the motor’s power is approximately 5.6 KW, with a phase current of 10.5 A.
Reply #42018-04-08
The rated voltage and rated current are reduced to 1/3

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.