Inverter constant power control mode

2019-06-17View Original

Thread Content

ABB ACS880 inverter, 30KW motor; the motor’s nameplate indicates a constant power range of 50–100Hz; Constant torque 5-50Hz. Since this is the first time setting the constant power control mode, which parameters need to be set?
Reply #22019-06-19
Set 12.30 to 100, and 30.14 to 100. The parameters for series 99 should be set according to the motor’s nameplate; all other settings remain the same as those for constant torque mode

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.