How to design the hydrogen vent pipe along with the lightning rod installation

2020-05-09View Original

Thread Content

The hydrogen vent pipe is 15 meters above the ground level, and lightning protection measures are required. How should these measures be implemented? As required by the lightning protection design codes, it is definitely not sufficient to use a single lightning rod. Should multiple lightning rods or conductors be installed?
Reply #22020-05-09
How can hydrogen allow venting? Adding a lightning rod is useless; a flame arrester needs to be installed.
Reply #32020-05-12
Is it a metal tube? If it is a metal pipe, once a flame arrester is installed and proper grounding is in place, no lightning conductor protection is needed
Reply #42020-05-14
Hydrogen evacuation? Aren’t you worried in case the flow rate gets too high?
Reply #52020-07-21
The direct leads are grounded; as long as the resistance requirement is met, it’s fine.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.