Is it necessary to design a lightning rod for the roof motor to provide lightning protection?

2020-08-11View Original

Thread Content

It mainly refers to the second type of lightning protection buildings; motors are steel-based devices, and their wall thickness is generally greater than 4 mm, so they can function as lightning receptors on their own. However, according to Clause 5.4.1 of GB 50650 \"Code for Lightning Protection Design of Petrochemical Plants\", mechanical and electrical equipment should be located within the lightning protection area to avoid being struck by direct lightning. ”The motor also needs to be protected; can its ability to protect itself be considered part of the protection mechanism? All sea friends are welcome to discuss. {:1_90:}
Reply #22020-08-11
This post was last edited by Deep blue, azure on 2020-8-11 22:10. I think an additional lightning conductor is needed. Metallic equipment used as lightning conductors shall be static equipment, see Article 4.2.3.
Reply #32020-09-02
Indeed, the regulation states that pump motors are rotating equipment, but if I install a metal rain cover above the motor, can that rain cover be used as a lightning conductor?
Reply #42020-09-22
I don’t think it’s necessary; It’s sufficient to ensure that the motor itself is properly grounded ; Install SPD on the power distribution circuit
Reply #52020-09-30
In our office as well, there are different opinions: some think that the motor itself is suitable, others believe that since it is a rotating device it is not appropriate, and still others think that installing a rain cover on the motor to serve as a lightning conductor would work. The key is that it seems no authority has specified which approach to follow. :shut up:
Reply #62020-09-30
If motors or rain covers can be used as lightning rods, it is best to avoid using separate lightning rods; after all, directing lightning down is also an uncertain factor. More importantly, this approach allows for savings in terms of the space required for the lightning rods and the associated costs
Reply #72020-10-01
I think a rain cover would work, but it should meet the requirements regarding materials as specified in GB50057 – such as thickness, down conductors – and it must also be securely connected to the metal storage tank.
Reply #82021-08-24
In actual engineering design, regarding the lightning protection for tank top motors, is it necessary to use rain guards (with thickness meeting the requirements of GB50650-2011) as protection for motors of rotating equipment? I’m urgently seeking advice, as a chemical processing project is facing a similar issue
Reply #92021-08-27
Isn’t it necessary to check the rolling radius first? If it’s not even within the range, then what’s the point of setting it?
Reply #102021-08-31
It must have been verified that protection is needed before this post was made; I’m curious to hear your insights
Reply #112021-09-01
50650 actually doesn’t have any ambiguity; since it is stated that electrical installations should be protected from direct lightning strikes, it is obvious that the components of electrical equipment cannot be exposed to such strikes. As for the rain cover, it’s something that doesn’t have a strict definition, I guess. The rain cover you made to meet the specifications of the lightning receptor can certainly be used as a lightning receptor~ But I’m still curious: how much does this motor need to protrude for it to require separate lightning protection? By how much is it higher than the surrounding railings? Could you provide a photo or sketch so I can take a look?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.