Find a phase sequence protector in which the relay does not activate when power is applied

2020-09-18View Original

Thread Content

Ordinary phase sequence protectors on the market have their relays engage when power is supplied, indicating that the power supply is normal; when there is a missing phase or phase imbalance, the relay disconnects, signaling a fault. The relay also stays disconnected when there is no three-phase power supply. What I need now is a phase sequence protector whose state remains the same whether the power supply is normal or not, with only a difference in state when there is a missing phase or a broken connection. Ideally, the relay should stay engaged when the three-phase power supply is normal or when there is no power at all (an auxiliary power source can be used); it should only disconnect in cases of missing phases or broken connections. Has anyone used such a voltage detector or phase sequence protector?
Reply #22020-09-28
It seems the state you’re looking for isn’t common
Reply #32020-09-30
I’m curious – if you have no electricity left, where does the electricity come from to enable it to attract things?
Reply #42020-09-30
You can weld a logic circuit board by yourself to output a closed signal when all the signals from the three mutual inductors are present, or a disconnected signal when one of them is missing; it should be available on Taobao
Reply #52020-09-30
You can weld a logic circuit board by yourself to output a closed signal when all the signals from the three mutual inductors are present, or a disconnected signal when one of them is missing; it should be available on Taobao
Reply #62020-09-30
Or you can use two sets of relays, one set with three relays, for a total of six relays. The first group consists of three normally open switches connected in series, the second group consists of three normally closed switches connected in series, and then these two groups are connected in parallel

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.