Continue studying the guidelines for light oil: Regarding grounding requirements, metal tanks must be grounded to protect them from direct lightning strikes. There should be no fewer than ( ) grounding points, which should be evenly distributed around the perimeter of the tank; the distance between these grounding wires should not exceed 18 meters. The impulse grounding resistance of each down conductor shall not be greater than ( ). Answer reply available at: 2 locations ; 10Ω
Reply #22018-08-31
The metal tank should be grounded to protect it from direct lightning strikes; there should be no fewer than (2) grounding points, which should be evenly distributed around the perimeter of the tank. The distance between these grounding wires should not exceed 18 meters. The impulse grounding resistance of each down conductor shall not exceed (10Ω)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.