Fire protection distance for pressure spheres containing flammable liquids

2019-04-05View Original

Thread Content

For combustible liquid pressure spheres (non-liquefied hydrocarbons) with a boiling point above 45 degrees, what should be considered for the fire separation distance between spheres? At 1.0D? How should the distance between the spherical tank and the fire dike be determined? 3 meters or half the diameter of the spherical tank? Is there any basis for it?
Reply #22019-09-08
Normally, it should be 3 meters according to the regulations for the petrochemical industry; thank you
Reply #32020-03-13
Reference can be made to \"GB 50160 Code for Fire Protection Design of Petrochemical Enterprises – 2018 Edition\", which specifies requirements for both of the aforementioned distances

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.