Is the water at the bottom of the instrument air storage tank drained using a drain valve? How else can it be discharged?
Reply #22020-05-20
There shouldn’t be any water in the instrument air storage tank; if water does precipitate, it’s best to drain it manually. If the water volume is variable, a steam trap is the best choice. Parallel installation is the most suitable option, for reference.
Reply #32020-05-20
Generally, a manual valve is added to allow for regular drainage; after all, there isn’t much water, and the drain valve might leak
Reply #42020-05-21
The required leak tolerance for instrument air is generally above -40°C; in cold regions, this requirement is even higher. Otherwise, as the temperature drops, water contained in the compressed instrument air will precipitate and accumulate in low points and dead ends, leading to problems such as freezing and blockages. The main measures taken by our company include: 1. Addressing the issue at its source by adding micro-heat regeneration desiccants and reducing leaks in the instrument air supply ; 2. Install an automatic water cut-off device; add electric heating and solenoid valves at the bottom of the instrument air buffer tank to cut off water regularly ; 3. Increase the frequency of inspections of instrument air to keep track of the real-time status of instrument air throughout the plant (our company has multiple air compressor stations) ; 4. Strengthen the air management for large-scale instrumentation equipment and critical instrumentation equipment ; 5. Strengthen the management of blind ends and low points in the instrument air pipeline network, enhance inspections, and drain the system as appropriate to prevent freezing and cracking incidents.
Reply #52020-05-27
Discharge regularly or install a steam trap. There should be no water in the instrument air tank.
Reply #62020-05-28
It’s your air separation dryer that has a problem; simply drain the water from the bottom of the tank regularly – there’s no need for a water strainer. In the north, it is recommended to add heat tracing at the bottom of the pipe, otherwise the pipes at the bottom may freeze and crack.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.