After the pump is stopped, why doesn’t the display on the control panel return to zero? It shows a value of around 0.03, with two digits after the decimal point – what’s the reason for this?

2017-06-23View Original

Thread Content

After the DCS control system stops the pump, why doesn’t the current return to zero? I would like to know what the reason is
Reply #22017-06-24
Both DCS and current transmitters have accuracy specifications; the readings do not necessarily drop to 0 once the pump is stopped, as long as they remain within the specified accuracy limits.
Reply #32017-06-24
This phenomenon has become* normal, but it’s not clear whether it’s actually normal or not.
Reply #42017-06-25
Generally, in electrical engineering, isolators are used to ensure safe isolation of signals when simulating them; there are zero-point and full-scale adjustment knobs on the isolator, which can be used for appropriate adjustments.
Reply #52017-06-26
There’s no problem, right? It can be adjusted a bit
Reply #62017-06-28
Just perform small-signal rejection

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.