I have a question regarding the configuration of the JX-300XP

2015-06-01View Original

Thread Content

The alarm configuration requirement for the IO point is SV:300 + DV:100 as an alarm, and DV:80 as another alarm. What does \"SV:300\" mean in this context? How do I set it up? ”+DV:100 alarm – does this mean that the \"high deviation\" setting in the deviation alarm settings is set to 100%? Thank you all
Reply #22015-06-01
SV:300 is a given value
Reply #32015-06-02
SV is the setpoint value, which refers to the desired value. DV is the deviation value, that is, the difference from the setpoint; generally, DV = SV – PV (the process measurement value), though different DCS manufacturers may have different definitions for this. +DV refers to the positive deviation alarm, that is, an alarm is triggered when the deviation is 100 or greater. -DV refers to the negative deviation alarm, that is, an alarm is triggered when the deviation is -80 or less. I have not used a central control system before, so this is just my personal understanding for reference only.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.