Problem of negative values displayed on the gauge pressure meter

2015-06-04View Original

Thread Content

The company has a Yokogawa gauge for absolute pressure, with a range of 0–100 MBAR. After it was installed, it showed -5 MBAR. Normally, an absolute pressure gauge should not display a negative value; what could be the reason? Is the zero point of the gauge incorrect, or is the vacuuming process too intense?
Reply #22015-06-04
Is it a 4–20mA signal? A negative value is displayed when there is no current signal (0mA); please check the current signal.........
Reply #32015-06-04
It outputs 4-20MA; if there is no current signal, it doesn’t mean the circuit is broken – so how can a negative value be displayed?
Reply #42015-06-04
Generally, in the absence of a current signal, that is, 0 mA, the gauge displays a negative value. The 4~20mA signal starts at 4mA rather than 0mA in order to facilitate fault detection, such as open circuits........
Reply #52015-06-04
The key point is that the on-site gauge also shows -5 mbar, which is consistent with the control room reading
Reply #62015-06-04
It’s clearly gauge pressure, so how did it turn into absolute pressure? Does it display 0 at atmospheric pressure (when the gauge is not installed)?
Reply #72015-06-04
There’s something wrong with your question – 0-100 Mbar is equivalent to a range of 0-10,000 MPa. Do sensors with such a large range even exist? It also shows -5Mbar, -500Mpa – are such pressures possible? The two of them are still arguing about the 4-20mA issue. . . I'm drunk too
Reply #82015-06-04
mbar millibar; otherwise there’s really a problem with the pressure
Reply #92015-06-04
:Case doesn’t matter for L; it’s deadly
Reply #102015-06-04
Well, the unit is millibar; it ranges from 0 to 100 millibar. When 475 is used, the current value displayed is 3.22 MA. The pressure is -4.8 mbar. What I mainly want to ask is: why does the gauge show a negative value? Is it zero-point drift, or is this indeed the negative absolute pressure value in the actual measurement?
Reply #112015-06-04
It’s the Yokogawa EJA310A gauge for absolute pressure, which shows an out-of-range reading at atmospheric pressure

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.