Our factory operates in the chemical chlor-alkali sector, and we have two hydrogen pumps in use. Around 6 a.m. that day, the temperatures of the bearings on both pumps rose suddenly; the temperature of one pump increased from 50 degrees to 98.1 degrees within five seconds before dropping again. The other one also rose, but it did not meet the trip condition. The temperature at the site did not actually rise; please analyze what kind of interference could cause this phenomenon?
Reply #22015-06-10
1. First, how do you determine that the actual temperature has not risen? 2. Check the grounding shield ; 3. Check the cable ; 4. To address such fluctuations, adding a transmitter at the sensor end improves interference resistance
Reply #32015-06-10
If the value rises within 5 seconds, check the records to see the interval between samples taken. DCS systems usually take samples every few seconds before sending data; observe the rate of increase. If the value rises within one or two sampling periods, possible causes include poor contact or the sensor touching the ground. If it indeed rises within about 5 seconds, consider whether there are high-power motors in the cable tray, especially those equipped with frequency converters. In such cases, it might be necessary to replace the transmitter with one from a reputable manufacturer like Siemens or E+H, as these models have excellent interference resistance
Reply #42015-06-10
  ∵The temperatures of the front and rear bearings of both pumps increased simultaneously, and those of the other pump also rose.   ∴It is highly suspected that abnormal process operation caused an increase in pump load.   The claim that the temperature at the site did not actually rise is untrustworthy; the sensors used to measure shaft temperature are inserted into the shaft bearings, so a short-term increase in temperature cannot be detected from the outside.  
Reply #52015-06-11
For these few temperature points, we are looking at the trend over one minute; it’s not visible on the chart, but it’s listed in the alarm messages as if it were an instantaneous value. There are many temperature sensors connected to this temperature card board, and the temperatures of all the others haven’t increased at all – it’s really strange
Reply #62015-06-11
The rise and fall of temperature is a slow process, but here it goes up and down in just a few seconds.
Reply #72015-06-11
After the trip, process technicians conducted on-site measurements and said the temperature was not high. Later, we ran this pump alone for over half an hour, and the temperature changed very little
Reply #82015-06-11
  You can’t apply the concept of using a container for heating to bearing shells. It can take just a few hundredths of a second for large machinery to go from normal operation to sudden bearing burnout.   You can go to the rotating equipment section to inquire about the temperature rise that occurs in cases of bearing failure and abnormal bearing cooling.   I once encountered a situation where an alarm was triggered due to high shaft temperature in a hydrogen compressor, but the cause could not be identified; after installing a flow switch at the pump outlet, the initial alarm that triggered in such cases changed from one related to shaft temperature to one related to flow rate.      The possible causes may vary depending on the situation; I’m just reminding you to pay attention to this aspect, as the actual identification of the cause will require on-site analysis.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.