How should clause 10.1.1 of GB50093-2013 be understood?

2015-07-07View Original

Thread Content

Regarding this specification, the wiring we designed uses steel pipes to carry the signals from the instrument junction boxes to the instrument locations; previously, grid frames were used for this purpose. I’m currently using a galvanized steel pipe supervision card, and they’re asking me to use explosion-proof union fittings. What should I do? Also, the instrument cables are all intrinsically safe. I think this specification is quite unreasonable – why should the acceptance criteria for instruments follow those for electrical systems?
Reply #22015-07-08
Upstairs, what is a grid fence? Do you have any pictures?
Reply #32015-07-08
10.1.1 This provision; The original poster has posted it; everyone, please take a look to help
Reply #42015-07-08
For the galvanized steel pipes coming out of the instrument junction box, ordinary union fittings are sufficient; there is no need for explosion-proof versions, as the instrument junction box itself is not completely sealed
Reply #52015-07-10
The picture should be available on Baidu. Common sizes are 100*50 and 200*100. It is a grid structure made by welding thin steel bars around 5 mm in diameter, which is then galvanized; the spacing between these bars is approximately 5 cm. Nowadays, many instruments use such grid structures at the branch points. Save steel. It’s cheap and very light.
Reply #62015-07-10
Currently, explosion-proof materials are more expensive than ordinary galvanized materials, and slip knots cost several times as much. Moreover, these regulations provide a basis for supervisors to extort money and demands; we supervisors end up having no argument left when faced with such demands.
Reply #72015-07-10
Is what you’re referring to called a basket-type cable tray?
Reply #82015-07-10
Never mind, put on the explosion-proof sealant………………
Reply #92015-07-10
Grid cable trays are generally referred to as grid fences

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.