Beginner seeking an example routine for analog output configuration

2015-08-17View Original

Thread Content

This post was last edited by Zor0 on 2015-8-19 10:48
Reply #22015-08-17
1. No, you need to change HI_LIM to 100. 2. Constants cannot be changed directly online; they must be modified and then reinstalled. Your MD10 is an intermediate variable, so of course you can’t manually modify its value.
Reply #32015-08-17
The sofa is right. Please refer to the attachment.
Reply #42015-08-17
So, what components should I use to implement this function (similar to a manual controller)?
Reply #52015-08-17
Try changing MD to a format like DB1.DD0, and also link the HMI to this address.
Reply #62015-08-17
If you don’t use HMI and instead modify the given values directly in the program, how do you configure it?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.