Pressure transmitter selection issues

2015-08-21View Original

Thread Content

The operating pressure of the equipment ranges from -10 kPa to 10 kPa (gauge pressure). A pressure transmitter needs to be installed – should it be a gauge pressure transmitter or an absolute pressure transmitter? ? If the gauge pressure transmitter range is set to -10~10? What about the range of gauge pressure?
Reply #22015-08-21
If the pressure is not high, a gauge pressure transmitter can be used; the operating range is between -10 and +10 kPa, and a transmitter with a range of ±15 kPa can be chosen. Personal opinion....
Reply #32015-08-21
It’s better to choose a transmitter with negative pressure; using a gauge pressure meter doesn’t seem to be a good option.
Reply #42015-08-21
For gauge pressure transmitters, if gauge pressure is to be used, a transmitter with a range of ±20 kPa can be selected
Reply #52015-08-21
A gauge pressure transmitter will do.
Reply #62015-08-21
  If the conditions specified for the process are -10 kPa to 10 kPa (gauge pressure), a pressure transmitter should be used, without considering absolute pressure transmitters.   Choosing a table based on process requirements is the right approach. In principle, if a gauge pressure gauge is to be used, the process operation design conditions must be changed first.  
Reply #72015-08-21
For gauge pressure transmitters, the operating range should be around 50% of the maximum scale limit; this is done both for safety reasons and to ensure optimal measurement accuracy and linearity.
Reply #82015-08-21
I will give priority to differential pressure transmitters, followed by pressure transmitters; I will not use gauge pressure transmitters. The negative terminal of the differential pressure transmitter is connected to the atmosphere, resulting in a gauge pressure output. The range must cover the pressure alarm values. @jiaguoyun
Reply #92015-08-22
This post was last edited by Fresh Sunshine on 2015-8-22 at 15:17. Since the requirement specified by the process engineering department is that the operating pressure of the equipment should be between -10 kPa and 10 kPa (gauge pressure), a pressure transmitter (gauge pressure) should definitely be used. A measurement range of -20 kPa to 20 kPa (gauge pressure) can be chosen, and most transmitters are capable of achieving this. Of course, a differential pressure transmitter can also be chosen, with a measurement range of -20 kPa to 20 kPa, and the low-pressure side is at atmospheric pressure.
Reply #102015-08-24
Gauge pressure is sufficient; the range can be selected based on the actual conditions on site. -15~15, -20~20 are both fine. Absolute pressure can be ignored, as the local atmospheric pressure is variable; therefore, even if it is measured, there will be some error.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.