Participation reward: 2 Wealth. Reward for correct answer: 9 wealth. Which of the following statements is correct regarding the airtightness and strength tests of the air ducts for air supply in air conditioners? ( ) (A). The airtightness test of air ducts can be carried out on the already installed air duct system. (B). Two connected sections taken from the fabricated air ducts are selected for testing. (C). The allowable air leakage rate for circular metal air ducts is 80% of the value specified for rectangular air ducts. (D) The strength test of air ducts should be conducted after the airtightness test has been passed. [Production and Management Division] Seeking moderators and technical discussants to join us
Reply #22015-09-30
Which of the following statements is correct regarding the airtightness and strength tests of the air ducts for air supply in air conditioners? (D) (A). The airtightness test of air ducts can be carried out on the already installed air duct system. (B) Two connected sections taken from the fabricated air ducts are selected for testing. (C) The allowable air leakage rate for circular metal air ducts is 80% of the value specified for rectangular air ducts. (D) The strength test of air ducts should be conducted after the airtightness test has been passed
Reply #32015-09-30
The answer should be: (D). The strength test of air ducts should be conducted after the airtightness test of those ducts has been passed, in accordance with clause 15.1.1 of the ‘Heating Installation’ standards. Before mass production of air ducts, tests for their strength and airtightness must be carried out. A is incorrect; according to clause 15.2.1, B is incorrect; clause 15.2.3 means C is incorrect; clause 15.2.4 means D is correct
Reply #42015-09-30
Which of the following statements is correct regarding the airtightness and strength tests of the air ducts for air supply in air conditioners? (D) The strength test of the air ducts should be conducted after the airtightness test of those ducts has been passed
Reply #52015-09-30
Which of the following statements is correct regarding the airtightness and strength tests of the air ducts for air supply in air conditioners? (A) The airtightness test of air ducts can be conducted on the already installed air duct system. (B) Two connected sections taken from the fabricated air ducts are selected for testing. (C) The allowable air leakage rate for circular metal air ducts is 80% of the value specified for rectangular air ducts. (D) The strength test of air ducts should be carried out after the airtightness test has been passed. Answer: D. According to clause 15.1.1 of the “Heating Installation” standards, strength and airtightness tests must be conducted on air ducts before they are manufactured in bulk. A Error ; Article 15.2.1 stipulates that B is incorrect ; 15.2.3 Clause C is incorrect ; Clause 15.2.4 D is correct.
Reply #62015-09-30
A:victory::victory::victory::victory:
Reply #72015-09-30
Which of the following statements is correct regarding the airtightness and strength tests of the air ducts for air supply in air conditioners? (D) (A). The airtightness test of air ducts can be carried out on the already installed air duct system. (B) Two connected sections taken from the fabricated air ducts are selected for testing. (C) The allowable air leakage rate for circular metal air ducts is 80% of the value specified for rectangular air ducts. (D) The strength test of air ducts should be conducted after the airtightness test has been passed
Reply #82015-09-30
(D) The strength test of the air ducts should be carried out after the airtightness test of the ducts has been passed

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.