Thread Content

For a hot-water-type single-effect absorption chiller with a cooling water inlet temperature of 13.5°C and an outlet temperature of 9.8°C, and a flow rate of 640 m3/h, how is the cooling capacity of the lithium bromide unit calculated? Is that power?
Reply #22015-10-07
It should be specific heat capacity times temperature difference times flow rate
Reply #32015-10-13
2.37 million kcal/h 2753 kW
Reply #42015-10-18
(13.5-9.8)*640*1000/3600*4.1868=2754kw

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.