The nitrogen buffer tank in the indoor air compressor station of our facility is equipped with a safety valve, and the pressure release from this valve occurs directly inside the room. Which regulation should be followed to determine whether the pressure relief outlet should be led outdoors?
Reply #22015-10-07
Setting aside the regulatory issues for now, nitrogen is an asphyxiant gas; any pressure release inside a building will result in a nitrogen-rich environment there. If maintenance or inspection personnel enter such a space, it could lead to asphyxiation accidents. Since nitrogen does not pollute the environment, why isn’t releasing it into the atmosphere considered an option? I believe that pressure release inside a building is not in line with safety standards and represents a significant potential safety hazard.
Reply #32015-10-07
The analysis on the 2nd floor is very thorough; it indeed should be discharged outdoors! ! ! ! ! ! ! ! ! ! ! !
Reply #42015-10-07
No gas other than air may be released indoors.
Reply #52015-10-07
Refer to the oxygen station specifications, which stipulate that the outlet should be at a height of 4.5 meters above the ground level
Reply #62015-10-08
Although the probability of discharge occurring exactly during an inspection is very low, from a safety design perspective, it still needs to be connected to the outside
Reply #72015-10-08
From a safety design perspective, it should still be connected to the outside! ! ! Sometimes, the piping is done simply

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.