Atmospheric pressure tank level gauge

2015-10-21View Original

Thread Content

I would like to ask whether a pressure-rated storage tank (or a tank with a volume exceeding a certain threshold) must be equipped with two sets of level measurement instruments, and whether the measurement principles of these two sets must be different.
Reply #22015-10-21
You can’t say that. One set is used to measure liquid level, informing managers of the amount present ; One set is used to detect high and low liquid levels, in order to trigger the shutdown of valves and pumps; these are what are commonly referred to as level switches. Two sets are needed because the purposes are different.
Reply #32015-10-21
If you explain it this way, it will be understandable. Previously, experts who inspected the reservoir area raised the issues I just mentioned. At present, in our company’s atmospheric pressure storage tanks, in addition to the level gauges used to measure the storage volume, there are also level switches equipped with high-level interlock functions. Such a setup should meet the standards, right?
Reply #42015-10-21
According to the standards, this is the practice used nowadays.
Reply #52015-10-21
One set for measurement, one set for comparison
Reply #62015-10-21
One unit for local use and one for remote transmission; the local unit is used for on-site inspections, while the remote unit is used for control
Reply #72015-10-21
There is one unit for local use and one for remote transmission; this can be interpreted in two ways: for example, I can have a differential pressure level gauge on site to collect data, and this data can be displayed locally while also being transmitted to the control room. Additionally, the remote data source I use is a differential pressure level gauge, while the one for local display uses a magnetic flip board. Which one meets the standards!
Reply #82015-10-21
Which do you think is more reliable: a watch that displays the time locally and also transmits it over distance, or a combination of a remote-display watch and a local-display watch?
Reply #92015-10-21
If there’s a guarantee, then of course there’s no need to say anything. Wouldn’t it be great if it could meet the regulatory requirements while also being cost-effective?
Reply #102015-10-21
Generally, two liquid level measurement systems based on different principles are required to ensure a higher safety factor in case one of them fails or malfunctions. Additionally, they can also be referenced and compared with each other. As for cost-effectiveness, a simple and durable float can be chosen on-site. Choose a better type for long-distance transmission.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.