Is there any SIS system in which all DI points are isolated using relays (or isolators)?

2015-11-19View Original

Thread Content

Is there any SIS system in which all DI points are isolated using relays (or isolators)? It seems that the DI cards in the SIS system often report errors due to on-site issues.
Reply #22015-11-19
Generally, only the DI signals from electrical systems require relay isolation; The intrinsically safe DI signals from the field require an isolated safety barrier. I don’t know which SIS you use? It seems like this is the first time I’ve heard of such a fault phenomenon as you described.
Reply #32015-11-20
DI is connected to the card directly through insurance terminals; since there is no isolation safety barrier, is it necessary to install one? The site might experience a ground short circuit at times

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.