Why does the main catalytic fan have two vents?

2015-12-16View Original

Thread Content

What is the purpose and principle behind setting it? I didn’t understand the technical Q&A
Reply #22015-12-16
One is for venting during surge, and the other is a small vent for adjusting air volume
Reply #32015-12-17
They are all called anti-surge valves. If there’s anything you don’t understand, don’t use the outlet vent to adjust the air volume! Use the inlet or blade angle
Reply #42015-12-17
Have you checked the range of these two anti-surge control valves? If these two anti-surge valves are A and B, it is possible that valve A has a range of 0----50%, while valve B has a range of 50%-----100%; this can be confirmed through the logic of the safety system
Reply #52015-12-17
The situation you are referring to applies to axial flow main fans, where the volume of air flow is adjusted by changing the angle of the stationary blades; The air volume regulation of the centrifugal main fan is achieved through the inlet flow rate
Reply #62015-12-17
It’s basically in the form you described – it involves two circuits for step-controlled operation; here, however, it’s 0-50% and 40-100%
Reply #72015-12-19
You’ve also added a cross-check for your profit sharing, hehe. It is mainly for protective purposes only; its effect is not very significant
Reply #82015-12-20
Thank you. Is adjusting the air volume intended for centrifugal fans?
Reply #92015-12-20
One is for self-protection by rapid venting, and the other is for adjusting surge, right? Is it okay to design it as just one row?
Reply #102015-12-20
At the moment, one can only learn about it from books...
Reply #112015-12-20
For the exhaust of our centrifugal main fan, there is a manual exhaust valve and an electric butterfly valve. The inlet butterfly valve is used to control the air volume. During normal operation, the two vent valves are closed

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.