2016-01-22View Original

Thread Content

I have a set of integrated temperature and pressure reducing devices, which include a water control valve and a water isolation valve on the cooling water pipeline. The factory requires that the cooling water isolation valve be located at the front of the water pipeline, with the water control valve situated behind the isolation valve. What’s the point of installing it this way? If the isolation door is at the back and the adjustment door is at the front, what impact does such an installation have?
Reply #22016-01-25
Isolation valve, control valve, check valve – this is the normal sequence of arrangement

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.