HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Valve testing in pipeline installation

2016-04-08View Original

Thread Content

In the installation of pressure pipelines, it is required to conduct strength tests on the valve housings and seal tests on the valves. Flange connections can be easily tested, but how are welded connections tested? I would appreciate some expert advice, thank you!
Reply #22016-04-08
Valves are inspected first and then installed.
Reply #32016-04-08
Valve testing is carried out before installation, and installation proceeds only after passing the test.
Reply #42016-04-08
If you want to conduct a pressure test, it’s not impossible to do so: place pads on both sides of the valve, build a frame, and use a jack to apply pressure for the test
Reply #52016-04-09
Valve testing is specified in several standards for \"industrial pipelines\", but pressure tests are generally not carried out in practice. Please leave your comments
Reply #62016-04-09
There’s no such thing as a separate test; it’s just done by pressurizing the pipeline directly, thus completing the test in one go
Reply #72016-04-10
If the valve manufacturer has provided proof of a pressure test prior to shipment, it can be installed directly and subjected to a pressure test along with the pipes.
Reply #82016-04-10
Welded valves can only be pressure-tested after they have been installed and integrated with the piping system
Reply #92016-04-10
The project specifications for foreign clients require that pressure tests be conducted on the valves before they are transported to the site and installed in the pipelines, in order to prevent damage that may occur during transportation.
Reply #102016-04-11
Valves are usually installed only after passing tests such as pressure testing
Reply #112016-04-11
Valves shall be inspected before installation; the inspection items, quantities, and methods are clearly specified in 4.0.3 and 4.0.4 of the \"GB 50184-2011 Code for Acceptance of Construction Quality of Industrial Metal Piping Projects\". The testing of valves should be carried out using a dedicated test bench. For your reference, 4.0.3 Valves shall undergo shell pressure tests and sealing tests; valves with an upper sealing structure shall also undergo an upper sealing test, and they must comply with the following requirements: 1 Valve tests shall be conducted using clean water as the testing medium. When testing stainless steel valves, the chloride ion content in water must not exceed 25×10‑6 (25 ppm). Once the test is passed, the water stains should be removed immediately. When there are special requirements, the test medium shall comply with the provisions of the design documents. 2 The test pressure for the valve housing shall be 1.5 times the maximum allowable operating pressure of the valve at 20°C ; The sealing test pressure shall be 1.1 times the maximum allowable operating pressure of the valve at 20°C ; When the valve nameplate indicates that a high-pressure sealing test is not suitable for the maximum operating pressure difference or the actuator supplied with the valve, the test pressure shall be 1.1 times the maximum operating pressure difference indicated on the valve nameplate ; The upper sealing test pressure for the valve should be 1.1 times the valve’s maximum allowable operating pressure at 20°C ; The test pressure for the jacket portion of a jacketed valve should be 1.5 times the design pressure. 3 The duration under test pressure shall not be less than 5 min. 4 The pressure test of the valve housing shall be considered successful if there is no leakage from the housing gasket. The valve sealing test and the upper sealing test are considered successful if there is no leakage at the sealing surfaces. 5 Number of inspections: It shall comply with the following provisions: 1) Valves used in GC1-class pipelines and pipelines for Class C fluids with a design pressure of 10 MPa or higher shall be subject to 100% inspection. 2) For valves used in GC2 class pipelines and all Class C fluid pipelines with a design pressure of less than 10 MPa, 10% of each inspection lot shall be sampled, with a minimum of 1 valve per lot. 3) For valves used in GC3 class pipelines and Class D fluid pipelines, 5% of each inspection lot shall be sampled randomly, with a minimum of 1 valve. 6 Inspection methods: Visual inspection, examination of valve test records, and review of water quality analysis reports.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.