A DCS control room typically has several 220VAC power supplies. How many power supplies come from the distribution room? How are they connected? How is redundancy achieved? What about UPSs – how are they connected?
Reply #22016-04-21
4 channels, I’m not very familiar with it as a layperson. There are drawings
Reply #32016-04-21
There are two UPS systems: one connected to the mains power, which feeds into the DCS power distribution cabinet; power redundancy is achieved through the DCS power supply modules
Reply #42016-04-21
Currently, it is generally required to have dual UPS power supplies, in addition to a single mains power supply. The dual UPS systems achieve redundancy through power modules and fast-switching modules; the other power supply is used for cabinet lighting and fans.
Reply #52016-04-21
Generally, two UPS units are used; an additional mains power supply is provided for critical applications
Reply #62016-04-21
Generally, there are two independent UPS power supplies; depending on the actual needs, it is also possible to use one UPS and mains power. Special attention should be paid to the requirement that the operator station must be powered via two power supplies after passing through a quick-switching device!
Reply #72016-04-21
Option 1: It can be powered by a dual-UPS system, eliminating the need for mains electricity. Option 2: Dual UPS power supply + mains power. Mains power is used to supply electricity for the fan and lighting.
Reply #82016-04-21
One mains power supply and one UPS are sufficient; The mains power itself is dual-redundant
Reply #92016-04-21
UPS units are available with and without redundancy; if redundancy is required, choose a UPS unit with redundancy. The redundant UPS also provides power; in the end, what reaches the DCS is power from both the UPS and the mains supply. There are 2 routes in total
Reply #102016-04-24
In places that are not particularly important, one UPS and the mains power supply are used; in important locations, two UPS units along with the mains power supply are installed. The decision depends on whether a power outage could lead to serious hazards or significant financial losses!
Reply #112016-04-24
We all use two power sources: one is a UPS and the other is mains electricity

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.