For four-nozzle water-coal slurry gasification, has the safety interlock system been tested with feed under load as well? How was it done?
Reply #22016-05-30
The interlock test should involve sending fake signals from the instrument backend to check whether the interlock is triggered. If feeding is done under load, then it’s probably a trial run. . .
Reply #32016-05-31
This post was last edited by *aodouzi on 2016-5-31 20:00. The load test aims to determine the response time of the valve under pressure differences, thereby establishing the sequence for starting up the system. The valve actuation time should be checked from the SOE, not from the alarm records, as there is a time difference between the two, which can lead to misinterpretation.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.