I have a question regarding the startup procedure for two small Roots blowers, one in use and one as a backup

2016-05-30View Original

Thread Content

For aeration in wastewater treatment, two Roots blowers are used, one in operation and the other as a backup, with a power capacity of around 3 kW each. I want to automatically control two fans to operate in turn, but the manufacturer says it is not recommended to start the fans under load. Do I need to add an automatically controlled vent valve? Or rather, using a \"unloading valve\" (but I couldn’t find one suitable). I hope experienced experts can offer their suggestions! Thank you so much!
Reply #22016-05-30
Or in other words, can it be started directly when switching?
Reply #32016-05-30
A delayed startup method can be considered: after the currently in use unit stops (after a set period of time), the backup unit starts up. The pressure is basically relieved.
Reply #42016-05-30
But there is still water pressure at this time (the water depth is 3m); I’m not sure if I’m right……
Reply #52016-05-31
Setting the startup interval to 30 seconds will do; that way, there will be no pressure
Reply #62016-05-31
I’m sorry, I still don’t understand… I think there will still be load at the time of startup; it is a start-up under load. The fan manufacturer recommends using an automatic unloading valve
Reply #72016-05-31
Then install one according to the manufacturer’s requirements; since the fans have already been purchased, it doesn’t matter if there’s one less valve
Reply #82016-06-15
Increase the pressure by 29.4 kPa; if check valves are installed at the outlets of each fan, it is possible to start the units under load
Reply #92016-06-15
Increase the pressure by 29.4 kPa, provided that each fan pipeline is equipped with a check valve. It can be started
Reply #102016-06-15
If the fan’s outlet pipe is protected by a check valve, it can be started directly

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.