Are PLC analog input modules active or passive?

2016-06-20View Original

Thread Content

Some of the meters on site send signals of 4 to 20 milliamps to the PLC; the components that receive these signals are definitely analog input modules. I want to ask who provides the 24 volts – since it’s a two-wire system, I don’t see any 24-volt supply in the analog input modules.
Reply #22016-06-20
If it is a two-wire instrument, check to see if there are no safety barriers or signal distributors in the control room; if such devices are present, then it is they that supply the power
Reply #32016-06-20
The 24V power supply for the field transmitter should be powered directly by a 24V DC power source, with the power supply connected in series within the 4–20mA circuit.
Reply #42016-06-20
If you are a Siemens 7KF02 module, then you need to adjust the small jumper squares on the side.
Reply #52016-06-20
Generally, they are powered by a dedicated 24V power supply.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.