Are the temperature and pressure compensation formulas the same for different flowmeters? What are the different ones? Is there a universal formula?

2016-08-06View Original

Thread Content

Regarding the temperature and pressure compensation formulas for steam, I only know one for orifice plate flowmeters. I’m not sure if other types of flowmeters are the same. Do all manufacturers’ systems come equipped with built-in temperature and pressure compensation formulas?
Reply #22016-08-06
As far as I know, the instruments that require temperature and pressure compensation for measuring steam include pressure-taking elements such as orifice plates, along with flow meters of types like differential transmitters, vortex flow meters, and target flow meters. Some of these flow meters are integrated in design; they come equipped with built-in temperature and pressure sensors, and after processing the data through a gauge head, they output a flow signal that has been compensated for temperature and pressure effects. Some are separate; in DCS, temperature and pressure compensation calculations are required, and DCS manufacturers generally provide dedicated modules for this purpose.
Reply #32016-08-06
Different media require different formulas; you cannot use the ideal gas law to account for the flow rate of superheated steam – there is no universal formula.
Reply #42016-08-06
Gases: There is only one formula for temperature and pressure compensation, the ideal gas law. Different measurement methods are different. Tables or DCS can both be used for compensation; if DCS is not available, one can simply create it oneself.
Reply #52016-08-12
Density is an important parameter in steam flow measurement, and its accuracy determines, to a certain extent, the accuracy of the steam mass flow measurement. **Currently, there are no relevant regulations or standards for the calculation of steam. The main density calculation methods currently used for steam metering include: table lookup, the IFC67 formula, the IAPWS-IFC 1997 formula, PVT equation calculations, and custom-fitted formulas. The IFC67 formula and the IAPWS-IFC 1997 formula are both international standards. The basic results calculated by the first three methods are similar, while the PVT equation shows a significant deviation from these methods. DCS is designed primarily for control rather than precise measurement; therefore, the temperature and pressure compensation in DCS relies largely on the PVT equation. In China, companies that are capable of using formula 67 for temperature and pressure compensation calculations are already considered quite good.
Reply #62016-08-13
Steam flow meters must have temperature and pressure compensation; most flow meters come with such compensation built in. Check the manual – if it’s not available, then compensation will have to be implemented in the DCS!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.