How to change the feedback for the Metso locator NDP1510

Thread Content

Besides adjusting up and down
Reply #22016-09-22
What’s the problem? Please explain in detail!
Reply #32016-09-22
4 milliamps when on, 20 milliamps when off; the corresponding feedback is 100% at 4 milliamps and 0% at 20 milliamps. However, the feedback I get is 0% at 4 milliamps and 100% at 20 milliamps
Reply #42016-09-22
If I correct the reaction, the feedback is correct; but it becomes a 4-millimeter safety shutdown and a 20-millimeter safety activation
Reply #52016-09-22
In the case of the forward and reverse action of a valve, it is usually sufficient to set the signal direction; feedback is based on the valve’s opening degree and no configuration is required. The valve position for 4MA fully closed is the same as that for 20MA fully closed – both are 0
Reply #62016-09-22
Just change the forward/reverse action of the valve position output in the system configuration

Submit a Project

Need technical support or have a project requirement? No registration needed.

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.