Should the control room door open inward or outward?

2016-10-19View Original

Thread Content

For the project I’m working on at the moment, there are two doors in the control room, and they open outward. The side door opening conflicts with the process pipelines. If it is designed to open inward, will it pass the inspection during the project acceptance?
Reply #22016-10-19
They should all be swing-out. Is there a conflict between the side door and the process pipelines? It doesn’t conform to the design standards; there are requirements regarding the distance between the control room and the production area, otherwise a bunker-style control room would be built.
Reply #32016-10-19
Are you referring to all of them, or only those under high temperature and pressure?
Reply #42016-10-19
It will not pass the fire safety inspection. If it’s done now and still needs to be corrected during the inspection, it’s better to get it done properly right from the start.
Reply #52016-10-19
I’m not a professional... but everything I’ve seen and heard suggests that doors should open outward
Reply #62016-10-19
I don’t understand; I just imagined it: Ah, the control room is on fire! Which valve outside needs to be shut off manually? The guys rush outside, and they bang open the doors leading outside; For doors that open inward, duang~duang~duang~, people get trapped inside, which slows down their ability to leave.
Reply #72016-10-19
Yes, that’s exactly what it means; doors that open outward are designed to facilitate escape. After the fire caused a power outage, I pushed it open and ran out; but if it opened inward, it would waste time.
Reply #82016-10-19
I also think it shouldn’t open inward. Tell the boss!
Reply #92016-10-19
The leader said that with some effort, it’s possible to make it. . . . . . . . It’s awkward

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.