This post was last edited by Wang Tianze on 2016-10-25 at 00:58. There is a pneumatic differential pressure transmitter with a range of 20 KPa, corresponding to a flow rate of 40 t/h. What is the output of this transmitter when the flow rate is 30 t/h? Answer: Since there is a square root relationship between flow rate and differential pressure, to determine the differential pressure from the known flow rate, squaring is required: (30/40)²×100% = 56.25%. The differential pressure output signal is: 56.25%×80 + 20 = 65 Kpa
Reply #22016-10-24
There is a pneumatic differential pressure transmitter with a range of 20 KPa, corresponding to a flow rate of 40 t/h. What is the output of this transmitter when the flow rate is 30 t/h? Answer: Since there is a square root relationship between flow rate and differential pressure, to find the differential pressure given the flow rate, one uses the square of (30/40)²×100% = 56.25%. The differential pressure output signal is: 56.25%×80 + 20 = 65 Kpa.
Reply #32016-10-24
The range is 20 KPA; getting a value of 65 KPA means it’s beyond the range, right? I really can’t understand the questions in the question bank
Reply #42016-10-24
I think it’s (Q_current/Q_MAX) squared = P_current/PMAX; (30/40) squared = P/20. So P=11.25, right? Please point out any mistakes. Thank you
Reply #52016-10-24
Did he ask you about the output current of the regulator?
Reply #62016-10-25
Yes, it must be 11.25kPA
Reply #72016-10-25
This question is very simple: the square of Q is proportional to the pressure difference!
Reply #82016-10-25
This post was last edited by YuYuDeYuYu on 2016-10-25 at 09:37. Instrument Question Bank: There is a pneumatic differential pressure transmitter with a range of 20 KPa, corresponding to a flow rate of 40 t/h. When the flow rate is 30 t/h, what will be the output of the differential pressure transmitter? Answer: Since flow rate and differential pressure are related by a square root relationship, to find the differential pressure given the flow rate, one needs to apply the square operation: (30/40)² × 100% = 56.25%. The differential pressure output signal is then 56.25% × 80 + 20 = 65 Kpa. There’s something wrong with this question; I don’t understand what the questioner is trying to express. Thank you
Reply #92016-10-25
It seems that he must have made a mistake; if the calculated output current is also incorrect, then his second calculation is completely unreadable! Think about it carefully again
Reply #102016-10-25
(30/40)^2=(p-20)/100-20; p=80×(30/40)^2+20=64.80

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.