Question about the range of a temperature transmitter?

2020-05-11 View Original

Thread Content

This post was last edited by wangduo1122 on 2020-5-11 at 17:39. It is specified that a temperature transmitter ranging from 0-150°C should be used; can it be replaced with one ranging from 0-200°C? For a transmitter operating in the 0-150℃ range, 20mA corresponds to 150℃; for a transmitter in the 0-200℃ range, 20mA corresponds to 200℃. Is it necessary to adjust the 20mA setting of the 0-200℃ transmitter to 150℃ if it is replaced?
Reply #2 2020-05-12
The range can be adjusted using a manual operator
Reply #3 2020-05-12
It needs to be changed to match the DCS range
Reply #4 2020-05-12
What was said upstairs is correct – the handheld controller’s measurement range can be adjusted; it can still be used without making any changes, as long as its range matches that of the DCS
Reply #5 2020-05-13
It entirely depends on whether the range of the signal reception end of the temperature transmitter matches the range of your temperature transmitter. If the reception end cannot have its range changed, then you will have to make the change yourself; if it’s possible to adjust the range accordingly, then it doesn’t matter from your side.
Reply #6 2020-05-16
The transmitter can remain unchanged, but the scale of the DCS needs to be changed. Or modify the transmitter range. The correspondence between the temperature sensing element and the temperature value remains constant. Taking a thermoresistor as an example: for transmitters operating in the range of 0–150°C, the corresponding input value is 100–157.33Ω; for transmitters operating in the range of 0–200°C, the corresponding input value is 100–175.86Ω. If a value of 157.33Ω is applied to a transmitter designed for the 0–200°C range, the output of the transmitter will correspond to a temperature of 150°C. For DCS, the original 4–20mA range corresponded to 0–150°C; when it changes to 0–200°C, the scale also needs to be modified. .
Reply #7 2020-05-19
Sure, just change the configuration range to be the same. At the site and in the control room, the measurement ranges must match

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.