One motor, two 185 power sources – how to connect them?

2017-08-03View Original

Thread Content

There is a 350kw motor on site, along with a control cabinet. Two 185 cables run from the control cabinet to the motor – how should they be connected? , what principle.
Reply #22017-08-08
The rated current of a 350kW motor should be around 700A; the 185 you mentioned is probably the wire diameter! The current-carrying capacity is around 370. I think the two cables should be used in parallel; I’m not sure if that’s correct.
Reply #32017-08-12
What’s the correct answer anyway! Looking at them, they are all high-voltage motors! I thought the voltage was just 380V
Reply #42017-08-27
The original poster really didn’t clarify their question. The motor has a power of 350kW, and the voltage level is not specified. Generally, motors with a power of over 160 kW use 6kV/10kV power supply, so it is certainly a high-voltage motor. But in fact, if variable frequency control is used (the poster mentioned a control cabinet, which is likely a variable frequency control cabinet), 350kW motors generally use low-voltage power supply (380V or 690V). At this time, it is reasonable to use two cables with an 185 cross-section connected together.
Reply #52017-09-19
There can be an inverter or star-delta starting, right?
Reply #62017-09-20
I once encountered a 350KW motor from Germany that was also controlled via frequency conversion; at that time, two 185 cables were connected in parallel for use.
Reply #72017-09-25
The two cables need to be connected in parallel to the motor terminals.
Reply #82017-09-26
The maximum power of 400V low-voltage motors can reach 630KW. If your 350KW system operates at 400V, a 185 duplex connection is a reliable way to connect the motor.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.