Is it normal for the metering and protection functions to differ for the same current transformer?

2018-03-29View Original

Thread Content

Is it normal for the motor outlet to share the same current transformer, with different secondary side metering and protection ratios?
Reply #22018-03-30
The current transformer ratios for the same motor are identical; the only differences lie in the accuracy levels required for metering and protection, as well as in their saturation curves. The metering requires a higher level of accuracy, while protection requires a lower level of accuracy.
Reply #32018-03-30
It’s common for the accuracy grades to differ; it’s the first time I’ve seen two sets with inconsistent secondary turns ratios

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.