Current is flowing through the cable ground wire

2018-06-13View Original

Thread Content

In the motor circuit of a friend’s company, the connection is delta-shaped on-site with both ends grounded; the cable length is approximately 200 meters. It was found in the distribution room that a current of 5A was flowing through the ground wire, while one inverter circuit had a current of over 20 amps. What could be the cause of this? The insulation of the cables is in good condition.
Reply #22018-06-13
The on-site grounding point and the grounding point in the power distribution room are not at the same location. The low-voltage power cables are grounded at both ends, and the slight voltage difference between these two ends creates a circulating current in the ground wire. Recheck the on-site grounding and measure whether it meets the requirements.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.