【Daily Question】Utilities - HVAC - 20191220

2019-12-20View Original

Thread Content

It is known that the friction factors of the two parallel pipe sections are 50 Pa/(m3/h)2 and 2.732 Pa/(m3/h)2. If the total flow rate is 437.7 m3/h, then the flow rate through the pipe section with a friction factor of 50 Pa/(m3/h)2 is ( ). A. 102m3/h B. 204m3/h C. 335.7m3/h D. 61m3/h Answer: A

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.