Problems encountered during the testing of the fire backup system

2021-02-26View Original

Thread Content

During the on-site testing of the fire backup system, as soon as the water pump was started, the diesel generator stopped operating. Asked the diesel generator manufacturer, and the manufacturer replied: The water pump is too large ; Asked the water pump manufacturer, and the manufacturer replied: The diesel generator is too small. What exactly is the problem?
Reply #22021-03-01
The causes were investigated one by one on site, and now water is flowing again. The cause of the problem has also been identified: it was due to incorrect settings in the factory specifications provided by both the manufacturer of the motor and that of the fire pump.
Reply #32021-03-02
Hello, could you please explain the specific situation? What is the capacity of the generator? What is the power of the water pump? Thank you
Reply #42021-03-27
Factory setting of indicators? Could you explain it in detail?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.