In design, this situation often arises – how do people solve it?

2017-03-12View Original

Thread Content

Appendix B of GB150.1-2011 states that rupture discs cannot be used alone in applications involving media with an extremely high, high, or explosive toxicity level. However, the devices we design often use hydrogen as a medium, which is explosive. Due to factors such as their own cost considerations, customers often request that blast discs be used on the equipment. In this situation, how should it be handled? Does anyone have any good solutions?
Reply #22017-03-12
It’s definitely not allowed to violate national standards! ! It doesn’t matter how users use it, but your design documents must be correct
Reply #32017-03-13
As a designer, you of course follow the national standards
Reply #42017-03-13
It seems to be used together with the safety valve
Reply #52017-03-13
The design must comply with national standards; in the event of any safety incident at the site, the design is examined first, followed by the construction process and operations. The documents provided to the owner must meet relevant specifications. It is possible to calculate for the owner what size burst disc can serve as a substitute for a safety valve; if the owner wishes to make changes, they should find their own construction team and supervisor
Reply #62017-03-13
Comply with the relevant requirements in the hydrogen station design specifications. .
Reply #72017-03-13
Used in conjunction with a safety valve; a branch pipe is installed between the burst disc and the safety valve, along with a check valve and a pressure gauge
Reply #82017-03-13
Is it possible to install only the safety valve...

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.