Orifice plate flowmeters cannot provide accurate measurements

2018-08-30View Original

Thread Content

The flow meter at the 1.0MPA steam outlet device cannot provide accurate measurements; the flow rate tends to increase when the amount of steam sent out is low. Process conditions: Pipeline DN350, temperature around 280°C, continuous operation, flow rate of 15–20 T/H. Could the experts please analyze what the cause is? The issue with the transmitter has been ruled out
Reply #22018-08-30
The maximum flow rate for a 350-mm pipe is 50 tons; your flow rate is too low, which results in inaccurate readings. It is recommended to use a 200-mm diameter pipe along with an E+H vortex flow meter, along with temperature and pressure compensation
Reply #32018-08-30
Orifice plate flowmeters have a low range ratio, resulting in large errors at low flow rates; it is recommended to use flowmeters with a higher range ratio for measurement, such as vortex flowmeters....

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.