Stability test of the roof of vertical cylindrical welded fixed-roof steel storage tanks

2019-08-06View Original

Thread Content

Regarding the \"Stability test of the roof of vertical circular welded fixed-roof steel storage tanks,\" GB50128-2014 states that \"for fixed-roof storage tanks that are not sealed, stability tests are not required if there are no specifications in the design documents.\" However, if such tests are required, it is unclear whether a negative pressure equal to 1.25 times the test pressure should be used, or whether the negative pressure resulting from draining the liquid to the lowest possible level should be employed, or some other value.
Reply #22019-08-06
7.4.6 It is clearly stated that for the stability test of fixed-roof tanks, water should be filled to the design maximum level and then drained to carry out the test. During the test, the pressure should be reduced slowly; when the negative pressure specified for the test is reached, it is considered successful if there are no abnormalities at the top of the tank. Design negative pressure value
Reply #32019-08-07
It’s clearly stated in the construction specifications; take a close look
Reply #42019-08-08
Which specification? It’s not mentioned in GB50128
Reply #52019-08-08
Which specification? It’s not mentioned in GB50128
Reply #62019-08-09
Looking at GB50341, it seems to be Appendix B and Chapter 12 of the main text
Reply #72019-08-16
This post was last edited by yujwlhh on 2019-8-16 at 10:30. Page 37, section 7.4.6 of GB50128 states clearly that for the stability test of fixed roofs, water should be filled to the designed maximum level and then the water should be drained to carry out the test. During the test, the pressure should be reduced slowly; when the negative pressure specified for the test is reached, it is considered successful if there is no abnormal deformation at the top of the tank. Designed negative pressure value = Test negative pressure
Reply #82019-08-16
On page 37 of GB50128, section 7.4.6 states clearly that for the stability test of fixed roofs, water should be filled to the design maximum level and the test should be conducted by draining the water. During the test, the pressure should be reduced slowly; when the negative pressure specified for the test is reached, it is considered successful if there is no abnormal deformation at the top of the tank. Designed negative pressure value = Test negative pressure
Reply #92019-08-16
We have a water tank, and the manufacturer’s drawings do not provide for negative pressure

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.