How to deal with red boiler water

2019-11-28View Original

Thread Content

We have 2 2T steam boilers; one uses soft water as feedwater, while the other uses condensed water as the main feedwater, with soft water serving as a supplement. The boiler water color is normal in boilers using soft water, while it turns red and cloudy in boilers using condensed water. After the boiler water is left to settle, there is a red precipitate at the bottom. I’d like to ask what went wrong and how to fix it
Reply #22019-11-29
The pH of the condensate water is 5.5, and it occasionally turns slightly reddish in color
Reply #32019-11-29
A measure has now been taken to add sodium carbonate to the condensate recovery tank in order to increase its pH value; it is not clear whether this will work.
Reply #42019-11-29
We encounter many such cases here; since measures have not been taken to remove iron ions from the condensate water, the condensate contains iron ions, which causes the water in the boiler to turn red and form rust. You can contact me for help in removing these iron ions; my phone number is 18861090609
Reply #52024-03-28
Steam condensate is very pure, similar to distilled water, but it has poor buffering capacity; its pH level is often low, making it acidic. Weak acid corrosion and oxygen corrosion lead to elevated levels of iron ions in the steam condensate. If this untreated condensate is reused in boilers, the colorless ferrous ions are oxidized to ferric ions when heated in the boiler. As the water in the boiler becomes more concentrated, the iron ion concentration increases, causing the water to turn yellow or red. Iron ions can form iron oxide scale on the heating surfaces of the boiler, as well as cause corrosion beneath that scale. Refer to the following example for details: 3 solutions to the red color of acidic steam condensate. The source of acidity in steam condensate: Steam condensate is similar to distilled water, and its pH value is generally around 7, indicating neutrality. In boilers that use demineralized water for water supply, ammonia is added to raise the pH level of this demineralized water. Ammonia enters the boiler along with the water supply, vaporizes when heated, and then enters the heat exchanger as steam. There, it condenses again and dissolves into the condensed water, thereby raising the pH level of the condensed water to 8 or above. Under normal circumstances, however, the pH level of steam condensed water is around 5.5–6.5, and it is usually acidic, with a value below 7. ▲On July 2, 2022, the color of the acidic steam condensate water from a certain facility was red. The main reason for the low pH value of this steam condensate water, making it acidic, was the presence of dissolved CO2 in the water. When CO2 dissolves in water, it forms weak carbonic acid. Since steam condensate water is very pure and has poor buffering capacity, experiments have shown that at 25°C, when 1 milligram of carbon dioxide dissolves in 1 liter of pure water, the pH value of that pure water drops from 7.0 to 5.5. ▲On July 2, 2022, the color of the acidic steam condensate water from a certain facility was red, with a pH value of 6. There are two sources of carbon dioxide in steam condensate water: one is its dissolution from the air. Air contains 0.03% carbon dioxide, which dissolves into the steam condensate water through the raw water or open steam condensate recovery systems, resulting in a lower pH value and an acidic nature of the steam condensate water. The second source of carbon dioxide in steam condensate comes from the high levels of carbonate or bicarbonate ions in the boiler feed water; after sodium ion exchange softening of this feed water, carbonates and bicarbonates (such as sodium carbonate and sodium bicarbonate) remain in the water. Carbonates and bicarbonates enter the boiler along with the make-up water and are heated to cause concentration; the carbonate and bicarbonate ions in the make-up water decompose when heated, with CO2 escaping and entering the steam system. At this point, sodium hydroxide is formed in the boiler water, giving it an alkaline nature. As temperature and pressure decrease, CO2 dissolves into the condensed water to form carbonic acid, causing the pH value in both the steam and the condensed water to drop and making them acidic. NSO3- → CO2↑ + H2O + SO32-; SO32- + H2O → CO2↑ + ON-. The hazards of acidic steam condensate and the reason for its red color: CO2 dissolves in the condensate to form carbonic acid, which lowers the pH of the steam condensate and makes it acidic, thereby generating H+. If the boiler system lacks deoxidization measures or if the efficiency of the deoxidizer is low, or if the steam condensate recovery system is open, oxygen present in the air at 21% concentration can dissolve into the condensate. Both H+ and dissolved oxygen act as cathodic depolarizers in corrosion cells, which **accelerates the corrosion of the anodic metals in the equipment and pipelines of the steam and condensate systems**. High-temperature acidic steam condensate can rapidly corrode the equipment and piping in steam and condensate systems; therefore, it cannot be reused in boilers without treatment. Corrosion causes the iron ion level in steam condensate to exceed acceptable limits; colorless ferrous ions are oxidized to ferric ions, and as the concentration of ferric ions increases, the steam condensate takes on colors such as yellow, pink, orange-red, red, dark red, and soy sauce-colored. This is also the reason why some newly installed boiler steam and condensate piping systems suffer from corrosion, perforations, and leaks after just 4-5 years. In accordance with the national standard GB1576-200 \"Water Quality for Industrial Boilers,\" water with an iron ion content exceeding 0.3 mg/L shall not be used in boilers. Visually, the steam condensate appears pure and transparent; however, when the level of ferrous ions is excessive, it is reused in the boiler without any treatment. As the ferrous ions enter the boiler along with the steam condensate, they are heated, concentrated, and oxidized to form colored ferric ions, which cause the color of the boiler water to turn red. In the cases of red-colored boiler water that I have encountered among steam boiler users, over 85% of them were due to excessive levels of iron in the steam condensate, which was reused in the boiler without proper treatment. Trivalent iron ions act as catalysts for oxygen corrosion inside boilers; they not only accelerate the occurrence of such corrosion but also lead to the formation of iron oxide scale. This scale causes under-scale corrosion as well. Iron oxide scale significantly reduces the heat transfer efficiency of the boiler tubes, and this reduced efficiency results in substantial waste of fuel energy, along with higher exhaust temperatures ; Iron oxide scale not only shortens the service life of boilers, but also, when it accumulates in large quantities within the boiler tubes, it can cause the tubes to expand due to overheating, thereby posing a risk of tube rupture and creating significant hazards to the safe operation of the boiler. ▲On July 11, 2022, the color and appearance of the acidic steam condensate wastewater from a certain facility were improved, becoming clear and pure. ▲ On July 11, 2022, the pH value of the acidic steam condensate wastewater from that same facility was adjusted to 8; the wastewater had a red color. There are three solutions to this problem. One of the solutions for the red color of acidic steam condensate wastewater is to add ammonia to the boiler feed water. Ammonia is weakly alkaline; when heated in the boiler, it escapes along with the steam into the steam system. The steam containing ammonia then cools down and condenses into water after passing through heat exchangers or other cooling devices. Ammonia dissolves in this condensed water, raising its pH value and making it alkaline. When the pH value exceeds 8, ammonia can completely neutralize carbon dioxide in the water, forming NH4HCO3. NH3 + H2O → NH4OH (reversible)
NH4OH + CO2 → NH4HCO3 (reversible)
NH4OH + NH4HCO3 → (NH4)2CO3 + H2O (reversible)

Adding ammonia to boiler feedwater offers the advantage of preventing the red color in acidic steam condensate. Ammonia is inexpensive and is a common pH regulator; when added to boiler feedwater, it dissolves in water to form a weakly alkaline solution that raises the pH of the boiler water. When heated in the boiler water, ammonia evaporates and enters the heat exchange equipment as steam. As temperature and pressure drop, ammonia dissolves back into the condensate. By adding ammonia to boiler feedwater, the pH of the boiler water, steam, and condensate can be increased, thereby neutralizing the corrosive effect of CO2 in acidic steam and condensate on system equipment and pipelines, as well as reducing the iron ion content in the condensate. Adding ammonia to boiler feed water helps to address the problem of red-colored condensate from acidic steam. Issues to be considered when using ammonia in boiler feed water to deal with red-colored condensate: 1. Adding ammonia can only control the weakly acidic corrosion caused by CO2; it cannot prevent oxygen-induced corrosion. In water-ammonia fed boiler systems, corrosion of steam pipelines, corrosion of heat exchangers, corrosion of steam condensate pipelines, and excessive iron ions resulting in a red color of the steam condensate are common problems ; Issues to be noted when adding ammonia to boiler feed water to address the red color of acidic steam condensate: 2. Ammonia has a certain corrosive effect, and it is also prone to releasing ammonia vapor; the storage and use of liquid ammonia represent a source of danger ; Issues to be noted when adding ammonia to boiler feed water to address the red color of acidic steam condensate: 3. The pH value cannot be maintained for long using ammonia, and a relatively large amount of ammonia is required. Ammonia is volatile and unstable when heated; in the vapor-liquid phase of steam boilers, there is more gas phase and less liquid phase. To maintain the pH level of the steam condensate return water and prevent corrosion in the return pipelines as well as excessive iron content, a large amount of ammonia must be added. This is also why an ammonia odor can sometimes be detected when collecting or discharging steam condensate return water ; Issues to be noted when adding ammonia to boiler feed water to address the red color of acidic steam condensate: 4. When an excessive amount of ammonia is added to the feed water, corrosion of copper occurs more severely in the presence of dissolved oxygen; copper-based heat exchangers, copper pipes, and related instrumentation are prone to corrosion ; Issues to be noted when adding ammonia to boiler feed water to address the red color of acidic steam condensate: 5. Long-term use of high doses of ammonia is detrimental to boiler operation, as excessive amounts of ammonia can cause corrosion. Ammonia is alkaline and accelerates the precipitation of calcium, magnesium, and other substances, leading to scaling in boilers as well as corrosion beneath the scale ; Prolonged use may cause corrosion in valves, pipes, and other components; therefore, its addition amount must be strictly controlled, and it should be adjusted appropriately while adding it continuously ; Issues to be noted when adding ammonia to boiler feed water to address the red color of acidic steam condensate: 6. The claim that adding ammonia helps control excessive iron ions in steam condensate return water is a fallacy. Adding ammonia can only control the weakly acidic corrosion caused by CO2; it cannot prevent oxygen-induced corrosion. Moreover, since ammonia is volatile and unstable when heated, there is more of it in the gas phase and less in the liquid phase, and it cannot be added in high doses over a long period of time. Therefore, adding ammonia can only partially alleviate corrosion in steam systems, with limited effect on reducing the iron ion content in the steam condensate return water. Colleagues, has your facility experienced situations where the pH level of the steam condensate from the steam boilers was low, indicating acidity? Has there been any instance where the color of the steam condensate was red or yellow, or where the iron content in the steam condensate was above the acceptable level? How did you solve it? What methods do you use for scale prevention and removal, as well as corrosion protection in boilers? Regarding issues such as adjusting the pH value of boiler feed water, red color of boiler water, hardness in return water, corrosion, scaling, and tube failures in boilers, corrosion in steam systems, excessive iron content in steam condensate, red color of acidic steam condensate, as well as testing and treatment of boiler water quality, Yan Hui from Beijing University of Chemical Technology at 18600475386 is always available for industry colleagues to discuss these problems and exchange experiences. Students are also welcome to share information on new technologies related to boilers, while colleagues can share their experience in managing and using boiler equipment. Everyone involved in boiler operations is invited to learn from one another in order to solve various practical problems associated with boilers. 3 solutions for red-colored acidic steam condensate. Solution 2 for the red color of acidic steam condensate – filtration using equipment for removing iron from high-temperature steam condensate. This equipment filters out the excessive iron ions in the condensate, allowing the color of the steam condensate to return to normal levels; as a result, the iron ions content is within acceptable limits, enabling the steam condensate to be reused in boilers safely. Disadvantages of equipment for removing iron from high-temperature steam condensate: High initial investment for such equipment ; Equipment for removing iron from high-temperature steam condensate occupies a large amount of space, and the operating and maintenance costs of such equipment are not worth it ; The filter media for high-temperature steam condensate iron removal equipment needs to be replaced every 2–3 years, and the cost of replacing this media accounts for about one-third of the total cost of the equipment ; Equipment for removing iron from high-temperature steam condensate cannot increase the pH value of steam condensate ; Equipment for removing iron from high-temperature steam condensate cannot address the corrosion caused by acidic steam and condensate on the equipment and pipelines in the boiler steam system and condensate recovery system; since corrosion in these systems persists, there will always be a source of iron ions. The iron removal via filtration by such equipment is only a temporary solution, not a permanent one. ▲Water samples taken during the treatment of red-colored acidic steam condensate return water in a certain facility in July 2022. Solution No. 3 for addressing the red color of acidic steam condensate – adding BF-31T steam condensate protector. To counteract the oxygen corrosion and weak carbonic acid corrosion caused by acidic steam and condensate on the equipment and pipelines in boiler steam systems and condensate recovery systems, the BF-31T condensate system protector, a product owned exclusively by Beijing University of Chemical Technology, is typically used to prevent corrosion from occurring. The BF-31T condensate system protector is the core technology in the Science and Technology Ministry Innovation Fund project “Zero-Waste Steam Generation Technology” undertaken by our unit. The BF-31T condensate system protector product passed the \"Registration by the China Boiler Water Treatment Association\" program in 2003. Technical advantages of BF-31T steam condensate protector in addressing the red color of acidic steam condensate: 1. BF-31T is an alkaline emulsive liquid agent that is volatile. When added to boiler feed water, it becomes weakly alkaline upon dissolving in water. When heated in the boiler water, BF-31T evaporates and enters the heat exchange equipment along with the steam; as temperature and pressure drop, it then dissolves back into the condensate. The mechanism by which the BF-31T steam condensate protector works is to form a protective film throughout the boiler system to isolate O2 and CO2, while also raising the pH level of the boiler water, steam, and return water. This approach effectively addresses the problems of oxygen corrosion and weak acid corrosion that are common in steam condensate. It eliminates the source of iron ions in the steam condensate at its root, thereby solving the issue of red-colored condensate. This corrosion-inhibiting mechanism provides both temporary and permanent solutions to the problem of excessive iron levels in the condensate; it not only brings the iron content within acceptable limits but also protects all the equipment and pipelines in the boiler system from further corrosion, perforation, or leakage, **thus extending the service life of the system’s equipment. Technical advantages of BF-31T steam condensate protector in addressing the red color of acidic steam condensate: 2. The BF-31T condensate system protector requires simple operating conditions in practical use; there are no requirements regarding condensate temperature or iron content. However, some equipment designed for iron removal does have requirements concerning condensate temperature and iron levels. The technical advantages of BF-31T steam condensate protector in addressing the red color of acidic steam condensate: 3. BF-31T, as a protector for condensate systems, exhibits excellent buffering capacity despite fluctuations in production load, and does not affect the performance parameters related to water treatment. Technical advantages of BF-31T steam condensate protector in addressing the red color of acidic steam condensate: 4. The cost of BF-31T steam condensate protector decreases as more of it is used within the system, and there are no issues related to wastewater discharge from backwashing or other cleaning processes. Technical advantages of BF-31T steam condensate protector in addressing the red color of acidic steam condensate: 5. Compared to the use of ammonia, BF-31T offers better performance; ammonia can raise the pH level of boiler water and steam, thereby preventing mild acidic corrosion. Ammonia is volatile, with more in the gas phase and less in the liquid phase; it requires large quantities and cannot prevent oxygen corrosion. The technology of using BF-31T steam condensate protector to control the pH value in boiler feed water possesses all the advantages of the ammonia addition process: it has a moderate cost ; It will not increase the salt content in the boiler water ; It is volatile and can protect the entire equipment and pipelines in the boiler steam-water system. The main components of the BF-31T condensate protector are neutralizers, film-forming agents, and other additives; it possesses film-forming and neutralizing capabilities, good stability, and a favorable vapor-liquid phase distribution ratio, enabling it to rapidly control system corrosion. Neutralizing amines serve to raise the pH of boiler feed water, furnace water, steam, and condensate, thereby preventing corrosion caused by the weak acids formed by carbon dioxide in water ; The film-forming agent creates a hydrophobic protective film in the form of a monolayer on the metal surface; the gaps between the molecules in this film are smaller than the cross-sections of carbon dioxide and oxygen, which prevents corrosion-causing gas molecules such as O2 and CO2 from coming into contact with the metal, thus avoiding corrosion of the metal ; A reasonable vapor-liquid phase distribution ratio can effectively distribute the treatment agent between the vapor and liquid phases in metal pipes, thereby effectively addressing metal corrosion in systems with both vapor and liquid phases. It is particularly suitable for the protection and anti-corrosion of equipment that uses steam intermittently. The technical advantages of BF-31T steam condensate protector in addressing the red color of acidic steam condensate: 6. BF-31T enables rapid coating of the condensate; the iron ion level (total iron content) in the condensate water reaches the specified standard within 72 hours. Acidic steam condensate with a red color also returns to a pure and transparent state within 72 hours, facilitating experiments using this chemical. It can completely replace deaerators and deoxidizers. Compared to the iron removal processes and other measures used in common equipment on the market, the BF-31T condensate system protector requires no substantial investment in fixed equipment, no costs for equipment operation and maintenance, and no expensive replacements for filter media (with a service life of around 3 years and total costs accounting for 20-30%). It not only protects the system’s equipment and pipelines, thereby extending the lifespan of the boiler system, but also eliminates the source of iron ions, completely solving the problem of red-colored acidic steam condensate. This allows high-temperature, pure steam condensate to be recycled back into the boiler for safe use, achieving an effective solution to iron removal in condensate. 3 Solutions for Red-colored Acidic Steam Condensate (Yan Hui)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.