Must a steam drum be equipped with an on-site level gauge?

2020-07-27View Original

Thread Content

The factory’s drum is not considered a boiler; it is equipped with a two-out-of-three high/low liquid level interlock, as well as local level gauges. But the local level gauges keep breaking, and the spare parts are extremely expensive; as a result, production is essentially carried out without those local level gauges. So the question is, can the local level gauge of the steam drum be removed?
Reply #22020-07-27
No. The damage has a reason for it; this is not a common issue. The right thing to do is to find the cause and resolve it. It is not advisable to remove it when a problem arises. After all, it is a pressure vessel, so it’s better to follow the relevant regulations. For reference.
Reply #32020-07-28
The level gauge (including the local level gauge), safety valve, and pressure gauge are the three main safety accessories of a steam drum – can they really be removed?
Reply #42020-07-28
It belongs to a primary instrument; it is a safety accessory for boilers as specified in regulations such as the inspection procedures for special equipment and various equipment safety laws
Reply #52020-07-31
No, it is designed to be displayed on-site as a monitoring device to ensure accurate readings even when other instruments fail to function properly; according to the regulations, it is not allowed to be removed
Reply #62020-11-09
It’s not allowed. **The Technical Specifications for Special Equipment TSG-G0001-2012, namely the \"Regulations on Safety Supervision of Boilers\" (Boiler Regulations), contain the following provisions regarding water level gauges:

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.