Issues with the foundation anchor bolts of the exhaust fan

2011-06-30View Original

Thread Content

This post was last edited by gjn1970 on 2011-6-30 at 14:09. During the installation of the exhaust fan, the civil engineering team made mistakes in the holes for the foundation bolts. The installation requirements specify that there should be a gap of 4–6 MM between the half-coupling of the fan’s bearing box and that of the motor. However, upon inspection, it was found that the gap between the outer wall of the motor-side bolt and the inner wall of the hole where the bolt is inserted is less than 10 MM; in some areas, the bolt is almost in contact with the wall (as the bolt hole is slightly skewed). It is no longer possible to move the bolt any further, as this would prevent the maintenance of the required maximum gap of 6 MM. But a 10MM gap is too small. There are two methods for this purpose: one is to heat the anchor bolts and bend them, with the bent portion located at least 150 MM below the foundation casting hole, and the bending angle being less than 20 degrees ; Another method is to enlarge the wall of the bolt hole on the side with insufficient clearance, using a chisel to do so carefully. However, the latter tends to cause the walls of the anchor bolt holes to become loose, resulting in insufficient bonding strength between the new concrete grout and the original concrete after grouting; moreover, the installation specifications for the former seem to also prohibit it. Since the concrete foundation has already been completed, it is impossible to demolish it and rebuild it. Which of the above methods is the best after making compromises? Are there any other good options?
Reply #22011-06-30
This post was last edited by —Lantian— on 2011-6-30 at 13:32. Both options are problematic; the material of the anchor bolts will definitely be affected after heat bending, but generally the impact isn’t severe if the temperature isn’t too high. The second option isn’t reliable, as the concrete grades are different. Comparatively, the second option is better; how can foundation bolts bend?
Reply #32011-07-01
The second method can be used. There are drilling machines available currently. Overall grouting can be carried out using high-grade grouting material.
Reply #42011-07-01
Agree with the view from the 3rd floor: drill holes and then fill them with high-strength grout
Reply #52011-07-02
The second method is good; today’s high-grade rapid-setting cements should be able to achieve the required strength and other properties.
Reply #62014-10-26
Water drills can be used for reaming.
Reply #72014-10-27
The second advantage is obvious: today’s high-strength grouting materials can meet the requirements without any problem

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.